Re-writing of field value
#1
This is for a C-Bus blind controller. To create an open stop close functionality button you set the group to a vaue of 98% and re-send that every time to the bus. This then means you have one [C-Bus] button to open, close or stop the blind.

Now, I need to replicate this in CQC

I have a button on the screen that sends a value of 98 and this works if the current value is not 98. here is the problem, CQC will not re-send the command when the field value is 98, even though I need it to do so.

How do I get CQC to always write the value?

I cant change the value to say 99 after a delay, as this will drive the blind to almost full open (100% is open, 0% closed, 2% has a special function and 98% is O,S,C).

Mick
Reply
#2
The field needs to be marked as 'always write'. Otherwise it assumes a write of the current value is redundant. That's one of the things you can seton the driver field as it is being registered.
Dean Roddey
Explorans limites defectum
Reply
#3
Well unfortunately, that aint going to happen because its an encrypted driver and Rohan has disappeared.

Is that something you can do Dean?

Mick
Reply
#4
Not really, no. He's still around, you might be able to talk him into making that simple change.
Dean Roddey
Explorans limites defectum
Reply


Possibly Related Threads…
Thread Author Replies Views Last Post
  Get Field Value via HTTP znelbok 3 1,267 06-11-2020, 03:43 PM
Last Post: Dean Roddey
  Timers Driver / Field Time Image / Seconds gReatAutomation 1 1,155 03-16-2020, 05:48 PM
Last Post: Dean Roddey
  If statement to check field value simplextech 10 3,554 01-27-2020, 01:32 PM
Last Post: Dean Roddey
  Zwave lock battery level indicator on Field Checkbox kfly 4 3,331 09-07-2019, 05:34 AM
Last Post: kfly
  Stupid question: How can I read a motion or other field state change ghurty 10 4,156 01-10-2019, 10:10 AM
Last Post: Dean Roddey
  Logic Server Field Limit zra 6 3,700 07-10-2018, 12:44 PM
Last Post: zra
  Changing Field Values in Devices Tab TurboSam 3 2,289 01-01-2018, 02:47 PM
Last Post: Dean Roddey
  If Field Exist? znelbok 5 3,698 11-18-2017, 01:03 PM
Last Post: Dean Roddey
  Writing to an external file from trigger event Ira 21 9,949 11-13-2017, 02:08 PM
Last Post: znelbok
  Simple field change trigger action Bugman 15 9,852 10-23-2017, 11:55 AM
Last Post: Dean Roddey

Forum Jump:


Users browsing this thread: 1 Guest(s)