RadioRa2 HVAC Issues
#11
BTW, there's no guarantee that this will fix the issue. I'm taking a guess at what the problem was. So it's possible it's still there. If so, you might need to open your RA2 system up to me temporarily to test against. You can change the name/password after I'm done, so it's safe enough.

Though some logging would probably help. The stuff you posted previously didn't seem to actually contain the anything related to the failure, so another attempt at catching one of the actual errors in the logs can be tried first.
Dean Roddey
Software Geek Extraordinaire
Reply
#12
OK I am on 5.2.920 now.
I deleted the driver and reloaded.

Similar issues as before but now it recovers so we are getting closer.

When I change SetPnt in CQC Admin, it changed in CQC Admin AND updated the Lutron app instantly
Then went to ???? but now it recovers and reconnects within 10 seconds.
Not sure what the "17" is.  
It returns "17" no matter what temp I choose.

The log also captured an instance of the CurrenTemp changing.  Same issue
Not sure what the "22" is.

LOG:
06/20 01:47:41-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20

{
    CQCGenDrvS, MEng.System.CQC.Drivers.Lutron.RadioRA2.DriverImpl.1879, Status/App Status
    No recent asyncs, doing active poll
}
06/20 01:47:47-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCGenDrvS, MEng.System.CQC.Drivers.Lutron.RadioRA2.DriverImpl.2384, Status/App Status
    Exception in poll. Err=Value '17' exceeds the limits for field THERM#HVAC_Upstairs~LowSetPnt
}
06/20 01:47:47-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.7696, Status/Lost Connection
    Driver 'Lutron_RR2-V2' has lost connection to it's device
}
06/20 01:47:47-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.7730, Status/Lost Connection
    Driver 'Lutron_RR2-V2' has lost its communcations resource
}
06/20 01:47:52-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.3829, Status/App Status
    Driver 'Lutron_RR2-V2' is trying to get its comm resource
}
06/20 01:47:52-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.3868, Status/App Status
    Driver 'Lutron_RR2-V2' has its comm resource
}
06/20 01:47:52-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.3886, Status/App Status
    Driver 'Lutron_RR2-V2' is trying to connect to its device
}
06/20 01:47:55-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.3928, Status/App Status
    Driver 'Lutron_RR2-V2' has connected to its device
}
06/20 01:48:15-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCGenDrvS, MEng.System.CQC.Drivers.Lutron.RadioRA2.DriverImpl.1879, Status/App Status
    No recent asyncs, doing active poll
}
06/20 01:48:35-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCGenDrvS, MEng.System.CQC.Drivers.Lutron.RadioRA2.DriverImpl.1879, Status/App Status
    No recent asyncs, doing active poll
}
06/20 01:48:46-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCGenDrvS, MEng.System.CQC.Drivers.Lutron.RadioRA2.DriverImpl.2384, Status/App Status
    Exception in poll. Err=Value '22' exceeds the limits for field THERM#HVAC_Master~CurrentTemp
}
06/20 01:48:46-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.7696, Status/Lost Connection
    Driver 'Lutron_RR2-V2' has lost connection to it's device
}
06/20 01:48:46-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.7730, Status/Lost Connection
    Driver 'Lutron_RR2-V2' has lost its communcations resource
}
06/20 01:48:51-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.3829, Status/App Status
    Driver 'Lutron_RR2-V2' is trying to get its comm resource
}
06/20 01:48:51-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.3868, Status/App Status
    Driver 'Lutron_RR2-V2' has its comm resource
}
06/20 01:48:51-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.3886, Status/App Status
    Driver 'Lutron_RR2-V2' is trying to connect to its device
}
06/20 01:48:54-CQCServer, CQCServer, CQCDrv_Lutron_RR2-V2Thread20
{
    CQCKit, CQCDriver_DriverBase.cpp.3928, Status/App Status
    Driver 'Lutron_RR2-V2' has connected to its device
Reply
#13
Given the numbers it seems like maybe you have the thermostat set to report C temps instead of F? 17C is 63F. 22C is 71F, both of which seem likely to be about correct for those things. If you do the high and it says something like 26 is out of range, that would pretty much prove it I think, since that's about 78 degrees.

You tell the driver what to expect in the config file, and I assume in the software you tell it what to report?
Dean Roddey
Software Geek Extraordinaire
Reply
#14
Well, the protocol sure seems to imply that the values are always reported in F scale, but those sure look like C temps. I assume you couldn't have left out the temp scale in the config file since it should throw an error if it's not there. But, if you did manage not to indicate it in the file and get away with that, it would end up being C. So check the config file and see if you indicated the F scale.
Dean Roddey
Software Geek Extraordinaire
Reply
#15
Photo 
I confirmed it is F in my config file (Below)  I also confirmed that it is F in the Lutron software.

I was thinking the same thing that is was a F vs C issue but the error values (17 & 22) never changed no matter the SetPnt I entered or the current temp

Version=4
ButtonCnt=10
Button=Keypad2,38:2,Trig
Button=Keypad_Test,38:1,Trig
Button=SHADE_SCENE_All50P,16:3,Trig
Button=SHADE_SCENE_AllClosed,16:4,Trig
Button=SHADE_SCENE_AllLower,16:6,Trig
Button=SHADE_SCENE_AllOpen,16:2,Trig
Button=SHADE_SCENE_AllRaise,16:5,Trig
Button=SHADE_SCENE_Privacy50P,15:3,Trig
Button=SHADE_SCENE_PrivacyClosed,15:4,Trig
Button=SHADE_SCENE_PrivacyOpen,15:2,Trig
DimmerCnt=9
Dimmer=SHADE_MasterSit_Cener,10:0
Dimmer=SHADE_MasterSit_Left,7:0
Dimmer=SHADE_MasterSit_LeftCenter,9:0
Dimmer=SHADE_MasterSit_Right,12:0
Dimmer=SHADE_MasterSit_RightCenter,11:0
Dimmer=SHADE_Master_LeftPatio,6:0
Dimmer=SHADE_Master_LeftSide,13:0
Dimmer=SHADE_Master_RightPatio,8:0
Dimmer=SHADE_Master_RightSide,14:0
LEDCnt=0
OccSensorCnt=0
SwitchCnt=0
ThermoCnt=3
Thermo=HVAC_Living,31:0,F
Thermo=HVAC_Master,35:0,F
Thermo=HVAC_Upstairs,30:0,F

It looks like there is different action numbers for F and C in the Lutron protocal doc. Is the driver using the correct ones?

I think it is:
Current Temp 1=F and 15=C
Setpoint 2=F and 16=C

I am still thinking it is not a F vs C thing because the error value does not change

I really appreciate your help. I hope we can find a solution.
Reply
#16
Doh! I'm looking for both sets, and I'm supposed to be taking one and ignoring the other based on what F/C value you selected, but I'm not. So I get one good set of values and one bad. So that's why it probably recovers eventaully is that it sees the F value last at some point.

Let me fix this and I'll post a driver pack for you to try. I guess the one I have doesn't send the C's at all.
Dean Roddey
Software Geek Extraordinaire
Reply
#17
Import this guy, then do a reconfigure on the driver to pick up the change.


Attached Files
.cqcdrvpack   RadioRA2WithFCFix.CQCDrvPack (Size: 33.67 KB / Downloads: 1)
Dean Roddey
Software Geek Extraordinaire
Reply
#18
Awesome I am excited to try it when I get home.

I have another RR2 question on events.

I want to capture a button press on a RR2 keypad and trigger a shade action.
I added the button in the client interface and selected Y to trigger
When I press the button I see it below


TIME: 01:03:01
cqsl.header
{
    v=1
    sysid=5102052CAD14814E-0E8F1D62AAFF468B
    class=cqsl.useract
    source=cqsl.dev:Lutron_RR2-V2
}
cqsl.actinfo
{
    evtype=ButtonPress
    evdata=Keypad_Test-1
}

But I can’t get it to trigger my action. I know it’s probably a syntax thing but I can’t figure it out
Attached is what I tried

Thoughts?
Reply
#19
Set the filter to IsUserActionFor, then set the moniker to the Lutron_RR2-V2 moniker, and the type to ButtonPress. Inside the action you'll have to check for that specific keypad, so you'll need to get the trigger info, so something like:

Code:
TrigEvent::GetUserActionVals(LVar:Type, LVar:Value)
If (System::Equals(%(LVar:Value), Keypad_Test-1))
   // Do what you want here
EndIf
Dean Roddey
Software Geek Extraordinaire
Reply
#20
Here is the screen shot. I did not upload


Attached Files
.jpg   IMG_0940 (1).jpg (Size: 314.45 KB / Downloads: 7)
Reply


Possibly Related Threads...
Thread Author Replies Views Last Post
  Raise / Lower Shades in Lutron RadioRa2 avtexan 3 447 05-27-2018, 08:55 AM
Last Post: Dean Roddey
  Aprilaire T-Stats Issues avtexan 5 828 04-17-2018, 06:07 PM
Last Post: khill
  New HVAC System - Nest? dgage 5 1,915 05-24-2017, 11:15 AM
Last Post: dgage
  Firmware issues on Harmony Hub? Dean Roddey 0 647 08-26-2016, 09:14 AM
Last Post: Dean Roddey
  taRiva cxn issues = maybe changing equipment to a dual-usage approach IVB 20 3,003 01-05-2016, 09:11 AM
Last Post: Dean Roddey
  Installation Issues with CQC 4.7.1 and WHS V1 kblagron 2 1,223 05-11-2015, 07:32 PM
Last Post: kblagron
  Issy issues solved??? Deane Johnson 1 1,023 01-20-2015, 05:54 PM
Last Post: Dean Roddey
  Logitech Squeeze Center Drive issues jmwhooper 11 2,985 10-06-2014, 01:56 AM
Last Post: jmwhooper
  HAI Omni Pro II Issues [SOLVED] avtexan 6 2,071 09-08-2014, 07:46 PM
Last Post: avtexan
  Replacement HVAC system pinballmark 6 3,638 11-18-2013, 07:48 PM
Last Post: dgage

Forum Jump:


Users browsing this thread: 1 Guest(s)